Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Design load with sizing factor is lower than Calculated design load [closed]

asked 2018-06-19 00:59:47 -0500

Saroop's avatar

updated 2018-06-19 10:39:22 -0500

My Design Load With Sizing Factor is 33.14 tons which is lower than my Calculated Design Load of 48.69 tons. I didn't input a sizing factor for my zones so it should be using a default value of 1.15, correct? Why is this lower than the calculated design load? The air flows have a similar trend.

image description

edit retag flag offensive reopen merge delete

Closed for the following reason the question is answered, right answer was accepted by Saroop
close date 2018-06-19 11:06:58.832386

1 Answer

Sort by ยป oldest newest most voted
2

answered 2018-06-19 02:45:00 -0500

No, if blank or zero, the Zone Cooling (heating) Sizing Factor will be replaced by the global Sizing:Parameters.

By default the Sizing:Parameters sizing factors are 1.25 for heating and 1.15 for cooling (corresponding to ASHRAE Appendix G), but you may have changed them. These can be viewed/set on the "Simulation Settings" tab:

image description

edit flag offensive delete link more

Comments

Thanks for the response. I didn't change the sizing factors in simulation settings, so they are using those values. 1.25 for heating and 1.15 for cooling. I now realized that I input a Cooling Design Air Flow Rate and that value is being for the sizing factor calculations.

Saroop's avatar Saroop  ( 2018-06-19 11:06:13 -0500 )edit

Ok glad you figured it out!

Julien Marrec's avatar Julien Marrec  ( 2018-06-19 13:46:02 -0500 )edit

Careers

Question Tools

1 follower

Stats

Asked: 2018-06-19 00:59:47 -0500

Seen: 183 times

Last updated: Jun 19 '18