Big gap between cooling energy from zone and from chiller
I am modelling VAV system with water cooled chiller.
When I look at Sensible Heat Gain Summary in OutputTable.html, total cooling removed by HVAC Terminal Unit Sensible Air Cooling[kWh]
is 815MWh. On the other hand, when I sum up the Chiller Evaporator Cooling Rate[W]
exported from Output:Variable
, it is 1345MWh which is much bigger.
Does anyone know what is causing this situation?
[Edit]
When I export Chiller False Load Heat Transfer Rate
, found that sum of them is 296MWh. However, still there is gap between cooling from zone and chiller. Does anyone know which data I should check?
The difference is likely coming for different factors: mostly latent cooling in the zone, pump heat (on the chilled water side), and fan heat (on the AirLoopHVAC)
Is it possible to export those three factor through
output:variable
?Also look at the water coil connected to the chiller.