COP of District Cooling Component

asked 2018-06-01 09:08:26 -0500

I have recently run a simulation that used the DistrictCooling component to model a Central Chiller that is external to the building.

However, after reading the Engineering Reference Manual and Input/Output Manual, I am unable to determine if the energy consumption calculated from the District Cooling component accounts for a COP. My assumption is that the energy values are just that required to satisfy the demand, without a COP. Is that the case?

I would like to know so that I don't discount the energy consumed again if a COP was accounted.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-06-01 09:42:57 -0500

You are correct, there is no COP applied to the reported district cooling loads.

edit flag offensive delete link more

Comments

Thank you for your quick reply.

JustinShultz's avatar JustinShultz  ( 2018-06-01 09:47:10 -0500 )edit