The Create Baseline Building measure will handle this for you, which uses the coefficients below. These come from page 3.221 (251) of the PNNL 90.1-2010 Performance Rating Method Reference Manual (and probably from COMNET and Title24 references too).
case control_type
when 'Constant Flow'
coeff_a = 0.0
coeff_b = 1.0
coeff_c = 0.0
coeff_d = 0.0
when 'Riding Curve'
coeff_a = 0.0
coeff_b = 3.2485
coeff_c = -4.7443
coeff_d = 2.5294
when 'VSD No Reset'
coeff_a = 0.0
coeff_b = 0.5726
coeff_c = -0.301
coeff_d = 0.7347
when 'VSD DP Reset'
coeff_a = 0.0
coeff_b = 0.0205
coeff_c = 0.4101
coeff_d = 0.5753
Since the project is using the performance path you don't need to follow the prescriptive requirements of subsection 5, just the mandatory requirements of subsection 4.
G1.2 Performance Rating. This performance rating
method requires conformance with the following provisions:
All requirements of Sections 5.4, 6.4, 7.4, 8.4, 9.4, and 10.4 are
met. These sections contain the mandatory provisions of the
standard and are prerequisites for this rating method...