Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Point of Use Electrical Hot Water Heater

asked 2018-05-24 15:18:11 -0500

updated 2018-05-24 15:18:40 -0500

What is the best way to model a Point of Use Electrical Hot Water Heater in OpenStudio?

I was thinking that I could setup several small electric hot water heaters with small water volumes and let them address the demand. Would this be appropriate or might there be a better solution?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-05-24 15:48:54 -0500

I'd do it the same way. You can directly assign a "Use Flow Rate Fraction Schedule" use to a WaterHeater:Mixed object without the need for a plant loop.

The I/O examples here actually list one that is pretty close to your needs, the one named "Stand-alone electric, tankless example", except you could change the "Ambient Temperature Indicator" to Zone and hook up your thermal zone to it, and it'll look like this:

WaterHeater:Mixed,                     ! Stand-alone electric, tankless example
      Tankless,  !- Name
      0.003785,  !- Tank Volume {m3}
      Hot Water Setpoint Temp Schedule,  !- Setpoint Temperature Schedule
      ,  !- Deadband Temperature Difference {deltaC}
      82.2222,  !- Maximum Temperature Limit {C}
      Modulate,  !- Heater Control Type {Cycle | Modulate}
      11712,  !- Heater Maximum Capacity {W}
      0,  !- Heater Minimum Capacity {W}
      ,  !- Heater Ignition Minimum Flow Rate {m3/s}
      ,  !- Heater Ignition Delay {s}
      ELECTRICITY,  !- Heater Fuel Type
      0.95,  !- Heater Thermal Efficiency
      ,  !- Part Load Factor Curve
      10,  !- Off-Cycle Parasitic Fuel Consumption Rate {W}
      ELECTRICITY,  !- Off-Cycle Parasitic Fuel Type
      0,  !- Off-Cycle Parasitic Heat Fraction To Tank
      30,  !- On-Cycle Parasitic Fuel Consumption Rate {W}
      ELECTRICITY,  !- On-Cycle Parasitic Fuel Type
      0,  !- On-Cycle Parasitic Heat Fraction To Tank
      Zone,  !- Ambient Temperature Indicator {Schedule | Zone | Outdoors}
      ,  !- Ambient Temperature Schedule
      <INSERT NAME OF THERMAL ZONE>,  !- Ambient Temperature Zone
      ,  !- Off-Cycle Loss Coefficient To Ambient Temperature {W/K}
      ,  !- Off-Cycle Loss Fraction To Zone
      ,  !- On-Cycle Loss Coefficient To Ambient Temperature {W/K}
      ,  !- On-Cycle Loss Fraction To Zone
      0.000379,  !- Peak Volumetric Use Flow Rate {m3/s}
      Hot Water Demand Schedule,  !- Use Flow Rate Fraction Schedule
      ;  !- Cold Water Supply Temperature Schedule

Of course, do change both the "Peak Volumetric Use Flow Rate" and "Use Flow Rate Fraction Schedule" to match your actual case.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2018-05-24 15:18:11 -0500

Seen: 207 times

Last updated: May 24 '18