Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Why is the infiltration design value not reporting in OpenStudio?

asked 2018-05-15 21:37:14 -0600

RCulham's avatar

I am creating a new model in the most current OpenStudio version, 2.5.0 with a fixed infiltration rate in air changes per hour. In the space type definition grid view, I placed an infiltration object from the library into the appropriate column, changed the name and then modified the flow parameter and selected the air change per hour option and used the always on schedule.

The output report shows no infiltration amount.

I am more familiar with using the IDF-Editor and modifying the EnergyPlus idf code in an text editor. I would do that, however the functionality of OpenStudio is required for other aspects of this work. Perhaps I have missed something simple?

edit retag flag offensive close merge delete

Comments

1

Is the spaceType for which you assigned the infiltration object actually used by a space, that in turn is in a thermal zone?

Julien Marrec's avatar Julien Marrec  ( 2018-05-16 02:50:36 -0600 )edit

2 Answers

Sort by ยป oldest newest most voted
3

answered 2018-05-16 12:03:43 -0600

updated 2018-05-16 12:04:16 -0600

Seems like either the infiltration object didn't get associated with the space type, or that space type isn't assigned to any thermal zones. The space type summary in the standard report will list how many spaces are assigned to a space type, and will list the internal loads objects assigned to that space type, including infiltration. If you assigned internal loads directly to a space they won't show up in this table.

Regardless of whether infiltration is added to space types or directly to spaces, the impact of it would show up in the "Outdoor Air" table, along with mechanical and simple ventilation. It lists the average, min, and max values. This table pulls from the EnergyPlus tabular data in the SQL results. The space type summary pulls from model input data in the OSM.

edit flag offensive delete link more
0

answered 2018-05-17 12:19:41 -0600

RCulham's avatar

I ran this project file with Ideal Loads checked for all of the Zones. I than ran the file with the HVAC systems enabled and in drilling down through the output data, the infiltration rate was being accounted in the energy simulation.

However, all of the cells in the EnergyPlus html output file tables Average Outdoor Air During Occupied Hours and Minimum Outdoor Air During Occupied Hours were blank. This is why I thought the infiltration object had not been applied.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-05-15 21:37:14 -0600

Seen: 772 times

Last updated: May 17 '18