OpenStudio - Roof Space

asked 2018-04-25 03:17:30 -0600

Dongmin's avatar

updated 2018-05-09 19:46:57 -0600

Hi all,

I have a single story office building to model, and I have an empty, flat roof space that is not ventilated at all.

I want to investigate how the thickness of this roofspace affects thermal performance of my building. So far I have assigned it a separate thermal zone, and also set it such that it is an unconditioned space.

Is this all I need to do to correctly model what I have?

Cheers in advance,

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-04-25 10:27:13 -0600

That, and assigning correct constructions. And even if not ventilated, assign some infiltration too, no envelope is perfect.

edit flag offensive delete link more

Comments

1

Make sure the space type for the space is setup so that there are no lights or plug loads in the un-conditioned space. You can either not have a building default space type, or if you do have a building default space type, then create a mostly empty space type and assign it to this space to override the default.


Also make sure that "Part of Total Floor Area" is not checked for the space. This won't affect energy consumption but will affect calculated EUI.

David Goldwasser's avatar David Goldwasser  ( 2018-04-25 11:32:37 -0600 )edit

Hum, your comment ends up being more complete than my answer :)

Julien Marrec's avatar Julien Marrec  ( 2018-04-26 02:52:36 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-04-25 03:17:30 -0600

Seen: 187 times

Last updated: Apr 25 '18