Water Heater:Heat Pump - Tank Doing Majority of Heating

asked 2018-04-12 17:43:58 -0600

Lindsey Gaunt's avatar

updated 2018-04-12 19:20:00 -0600

I'm modeling a Water Heater:Heat Pump in Openstudio and am having trouble with the attached tank doing ALL of the water heating. I've tried a couple of things like adjusting the capacity and volume of the tank down to 1, but that just seems to remove that load completely. I've also tried to increase the capacity of the DX Coil in the HPWH, but that had no effect. Any ideas??

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-04-13 13:27:50 -0600

Lindsey Gaunt's avatar

Solved my own problem!

Had to raise the compressor setpoint temperature higher than the tank setpoint.