Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Monodraught windcatcher IES

asked 2018-04-05 09:57:32 -0600

updated 2018-04-05 10:45:39 -0600

I'm having difficulty simulating a naturally ventilated space using the Monodraught windcatcher components. The model will run if I don't add any heat gains to the space, however if I add any heat gains the analysis fails due to:

"Instability in room. Possible remedies: reduce time step; set radiant fraction to 0; check gain and ventilation levels; reduce MacroFlo opening areas."

Does anyone have any ideas?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2018-04-06 08:31:59 -0600

Monodraught helped me get to the bottom of this. Should anyone have a similar problem in the future see below:

The thermal template assigned to the windcatchers and associated ducts should be "Monodraught WINDCATCHER/Duct" for some reason this was not being pulled in when adding the windcatcher components. Having manually loaded the template and applied it to the relevant spaces the model runs fine.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-04-05 09:57:32 -0600

Seen: 554 times

Last updated: Apr 06 '18