Monodraught windcatcher IES

asked 7 years ago

updated 7 years ago

I'm having difficulty simulating a naturally ventilated space using the Monodraught windcatcher components. The model will run if I don't add any heat gains to the space, however if I add any heat gains the analysis fails due to:

"Instability in room. Possible remedies: reduce time step; set radiant fraction to 0; check gain and ventilation levels; reduce MacroFlo opening areas."

Does anyone have any ideas?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 7 years ago

Monodraught helped me get to the bottom of this. Should anyone have a similar problem in the future see below:

The thermal template assigned to the windcatchers and associated ducts should be "Monodraught WINDCATCHER/Duct" for some reason this was not being pulled in when adding the windcatcher components. Having manually loaded the template and applied it to the relevant spaces the model runs fine.