Setup for primary air loop supplying to multiple AHU's in OpenStudio

asked 2018-03-13 12:58:22 -0600

rkbest's avatar

updated 2018-03-13 14:32:10 -0600

OpenStudio

I want to set up an outdoor air pretreat air loop with heating/cooling coils and a constant speed fan supplying preconditioned air to other AHU's. How do I setup such primary and secondary air loop? I am wondering about how to connect the AHU's on the demand side. image description Can this be set up in OpenStudio and how?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2018-03-13 15:29:05 -0600

updated 2018-03-13 15:42:36 -0600

EnergyPlus currently doesn't support an air loop serving multiple other air loops. There was work in that direction, but it appears to have stalled out.

See here for discussion of workarounds for that design.

edit flag offensive delete link more