Why both the heating and cooling load are reduced when decrease the thickness of ground slab in cold region?

asked 2018-03-13 03:07:59 -0500

gaofeng's avatar

updated 2018-03-13 12:29:31 -0500

When I used the Ideal load air system and reduce the thickness of ground slab, both the heating load and cooling load will reduce, but in reality the heating load should increase. The ground surface temperature was set as 2C lower than indoor temperature. and the building located in cold region. Heating and Cooling setpoint are 18C and 24C respectively.

I have tried to solve the problem, but it was still existed. only when I reduce the groud surface temperature to 10C in winter, this problem was rectified but the heating load was too large.

So if you guys have the project with ideal load air system, can you try to reduce the thickness of ground slad to see the heating load performance. Because this is the main suspect target in current.

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
1

answered 2018-03-13 04:53:24 -0500

Avi's avatar

I was seeing same anomalies in my model until I changed the ground model to kiva model. look at this and that answers for more data.

edit flag offensive delete link more

Comments

Thanks for your suggestion, I have used the foundation Kiva and the result is improved, I will go on adjusting. Many thanks~

gaofeng's avatar gaofeng  ( 2018-03-13 10:58:40 -0500 )edit