Warehouse space conditioned by fans - always on

asked 7 years ago

pksmith's avatar

updated 7 years ago

Hello,

This is a follow up to my previous post here

I am trying to model an unconditioned warehouse space (no mechanical cooling, only fans combined with interlocked sidewall louvers).

The fans are upblast fans and have a total combined capacity of 900,000 cfm (louvers on the sidewalls allow outside air back into the facility). These fans are constant volume and always on regardless of temperature.

The issue I was running into following @Avi 's suggestion was I would get an error along the lines of "Severe * CalcMixedAirSetPoint: Missing reference temperature setpoint for Mixed Air Setpoint Manager " if I only used a mass flow setpoint manager and not a temperature set point.

Preview: (hide)

Comments

@pksmith could you post a link to your model?

Avi's avatar Avi  ( 7 years ago )

@Avi, sure here is a dropbox link to the model (https://www.dropbox.com/s/5lg0wnr3elx...) Let me know if there is a better way to get it to you. Thanks so much for taking a look!

pksmith's avatar pksmith  ( 7 years ago )

@pksmith The link is broken

Avi's avatar Avi  ( 7 years ago )
pksmith's avatar pksmith  ( 7 years ago )

@pksmith now it works

Avi's avatar Avi  ( 7 years ago )

1 Answer

Sort by » oldest newest most voted
3

answered 7 years ago

Avi's avatar

As I see it you can delete the Setpoint Manager and run it as is. After all you use constant flow rate fans. I have checked it on your model it will not through any Errors just few Warnings stating that you don't have any control for that loop (which is the case) and that you can't do sizing without thermostat setting (again you hard sized the fans so no sizing needed to my best understanding).

Preview: (hide)
link

Comments

@Avi, I really appreciate you taking a look. Two follow up questions: 1. How do I delete the setpoint manager?, and 2. Does it matter if the cooling size parameters (and heating size parameter) remain with the default values or will that impact my model?

pksmith's avatar pksmith  ( 7 years ago )

@pksmith 1. when you hover with the courser over the SP a black triangle will appear click on it to delete the SP. 2. I believe it will not affect anything.

Avi's avatar Avi  ( 7 years ago )

Thanks so much!

pksmith's avatar pksmith  ( 7 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.