Warehouse space conditioned by fans - always on
Hello,
This is a follow up to my previous post here
I am trying to model an unconditioned warehouse space (no mechanical cooling, only fans combined with interlocked sidewall louvers).
The fans are upblast fans and have a total combined capacity of 900,000 cfm (louvers on the sidewalls allow outside air back into the facility). These fans are constant volume and always on regardless of temperature.
The issue I was running into following @Avi 's suggestion was I would get an error along the lines of "Severe * CalcMixedAirSetPoint: Missing reference temperature setpoint for Mixed Air Setpoint Manager " if I only used a mass flow setpoint manager and not a temperature set point.
@pksmith could you post a link to your model?
@Avi, sure here is a dropbox link to the model (https://www.dropbox.com/s/5lg0wnr3elx...) Let me know if there is a better way to get it to you. Thanks so much for taking a look!
@pksmith The link is broken
Strange, give this one a try
@pksmith now it works