Question-and-Answer Resource for the Building Energy Modeling Community
Get s tarted with the Help page
Ask Your Question
2

Any way to operate condenser loop without setting setpoint manager

asked 2018-02-27 20:29:12 -0600

katsuya.obara gravatar image

In my model, there are four two speed cooling tower with 3000kW capacity.
I want to control how many cooling tower should be operated not by setpoint manager. Instead I want to use PlantEquipmentOperation:CoolingLoad.
Does anyone know whether this is possible or any trick I can implement?
I add logic image I want to implement as below.
image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-02-28 23:19:01 -0600

TomB gravatar image

You can stage the cooling towers by setting the Plant Loop Load Distribution Scheme to SequentialLoad. You still need a SetpointManager of some sort on the supply outlet node. Choose one that best suits the details of the system you are modelling.

image description

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

 

Question Tools

1 follower

Stats

Asked: 2018-02-27 20:29:12 -0600

Seen: 133 times

Last updated: Feb 28 '18