Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

Economizer limit in eQUEST

asked 2018-02-14 14:40:38 -0600

mjadamss's avatar

updated 2018-02-15 08:38:29 -0600

Hello,

I am working on eQuest 3.64 and the project has an economizer that allows up to ~60% design airflow to be OSA.

Is there an input for eQuest that allows this maximum to be present without impacts DCV controls?

Thanks,

Michael

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2018-02-14 16:05:49 -0600

Molly Curtz's avatar

updated 2018-02-14 16:25:25 -0600

Yes. Use the keyword "Max-OA-Fraction" to set a limit on the fraction of OSA when economizer operates. This keyword input is available in eQuest as one of the economizer input boxes in the graphical user interface.

edit flag offensive delete link more

Comments

Thanks Molly! i have no idea how I neglected to see that input box!

mjadamss's avatar mjadamss  ( 2018-02-14 17:45:07 -0600 )edit