unable to reach set point temperatures in zones

asked 2018-02-10 15:18:40 -0500

Siva's avatar

updated 2018-02-12 13:33:00 -0500

Please see the below attached file of radiant cooling system served by a purchase cooling.

I designed as per Design Day conditons and I got the cooling load for set point temperature of 24 degC ....

Purchased cooling Design capacity: 14.876 kW Flow rate: 0.001772 m3/sec

when I simulated for the same city, I am not getting temepratures equal to that of set point.

These are the peak temperatures that I am noticing:

west Zone: 30.9572 degC

east Zone: 31.1degC

North zone: 28.67 degC

peak cooling capacity of Purchased cooling observed in simulation reports is : 35.2613 which is way higher than the design capacity 14.876 kW. Why is this? the peak capacity should not be greater than the design one right?

peak cooling zone capacities are

west zone: 12.414 kW East zone: 11.331kW North Zone: 12.707kW

where as the design capacities are

west zone: 4.454 kW East zone: 4.575kW North Zone: 5.846 kW Why is this? the peak capacity should not be greater than the design one right?

during what conditions I can see both the simualted peak capacity and design capacity same?

What should I do to pull down the temperatures to that of set points? eventhough it is not practical, I maintained the temperature of cooling water as 5 degC. I tried changing the capacity of purchased cooling. but it is limted to accept only upto certain capacities. beyond that it is not accepting...what should I do to pull down the temperatures?

edit retag flag offensive close merge delete

Comments

@Siva Please tag the application you are using. Do you have any latent cooling in your model. can you post the eplusout.err file?

Avi's avatar Avi  ( 2018-02-11 01:49:00 -0500 )edit

it seems I cannot attach the file.....I eliminated people load ....so there is no latent cooling....

Siva's avatar Siva  ( 2018-02-11 02:39:11 -0500 )edit

@Siva Just paste it into the end of your question (using Edit) and then mark it as code. Do you use outside air (infiltration or vent)?

Avi's avatar Avi  ( 2018-02-11 02:50:23 -0500 )edit

Yeah I have done that....those warnings are ignorable one.....No I have removed outside air, infiltration and people load.....I am just checking only the sensible load with radiant cooling system....I just want to start with that and later on thought of tackling condensation issues...

Siva's avatar Siva  ( 2018-02-11 03:12:40 -0500 )edit

@Siva could you post a link to your model?

Avi's avatar Avi  ( 2018-02-11 03:16:37 -0500 )edit