Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

which node referred for FaultModel:TemperatureSensorOffset:ReturnAir

asked 2018-02-07 21:41:39 -0600

building_performance's avatar

updated 2018-05-21 21:52:03 -0600

I try to use EMS module to implement the return-air-temperature-sensor-offset for OA-Mixer. (FaultModel currently has a bug). But I face a problem: which node is the reference point for the sensor offset? Thanks.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-02-08 05:19:20 -0600

updated 2018-02-08 05:21:12 -0600

As the name implies, it's the return air node.

An AirLoopHVAC:OutdoorAirSystem has four nodes:

  • Return Air Node
  • Relief Air Node
  • (Outside) Inlet Air Node (it gets air from a virtual "OutdoorAir:Node" that represents environmental conditions)
  • Mixed Air Node

OA System Node

All the air in the return path of the AirLoopHVAC gets to the Return Air Node, at which points a fraction can go to the Relief Air Node (to the outside) and the rest goes to the mixed air node. The mixed air node gets air from the return air node and the outside inlet node.

Source:

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2018-02-07 21:41:39 -0600

Seen: 95 times

Last updated: Feb 08 '18