How can I simulated blinds in the heating season, simulated Interior Shade during the cooling season?

asked 2018-01-17 22:58:12 -0600

HVAC-JAY's avatar

updated 2018-01-18 12:13:23 -0600

Hi, everyone. I've had some problems in Energyplus shading control setting. How can I simulated blinds in the heating season, simulated Interior Shade during the cooling season? Thanks. The software setup seems to set only one pattern, blind or shade, throughout the year.Thanks.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2018-01-18 00:13:40 -0600

bbrannon4's avatar

The easiest way would be to just make separate control/availability schedules for each based on the season. If you want to have more control then just defining manually what the heating and cooling season are, you could add in some EMS controllers with logic based on the outdoor conditions, solar gains, etc.

edit flag offensive delete link more

Comments

thank you,bbrannon4,I'll try to do such setting,schedules.

HVAC-JAY's avatar HVAC-JAY  ( 2018-01-19 01:33:06 -0600 )edit