radiant floor savings vary a lot Atlanta vs Pittsburgh
Dear UMH community, I have modeled two nominally identical buildings, one in Atlanta, Ga, the other in Pittsburgh, PA. While the wall & roof constructions differ, using the ASHRAE 90.1 definitions for the respective climate zone, the floor constructions:
- are identical for the heated floor portion (about 20% of the total floor)
- are identical for the unheated portion of the floor
- there is NO underfloor insulation (the heated slab is in contact with the earth below)
My results for Atlanta show substantial energy savings (~35%) compared to an ASHRAE baseline. Results for Pittsburgh, however, show only 6% energy savings. All of the difference is in gas usage for the hot water boiler.
That makes no sense to me. Can you make any suggestions regarding what to look at in order to understand the discrepancy? Thanks so much!
p.s., the IDFs have been extensively compared and I'm confident they're identical except for wall and roof constructions.
I'd start by comparing the weather files first - how do the outdoor conditions compare during the times when the savings happen? I suspect you'll find a trend there. Admittedly I don't know the Pittsburgh climate, but I'd expect Atlanta to be much hotter so require almost no cooling. If you look at absolute values, is Pittsburgh model saving more absolute energy, just a smaller percentage of the total? I'd also pull out conduction values by surface just to confirm that the savings is from conduction through the floor,
Pittsburgh has ~5400 HDD65, Altanta is ~2900 HDD65. What did you assume for your ground temperatures? What is your ASHRAE baseline system? And what are your boiler efficiencies? How did you set up radiant floor control in your model?
Thanks for the feedback; it's making me think differently about the results! answering some of the questions:
My earlier comparison of relative savings (%) was flawed (thanks!); I only need to look at heating energy. Any thoughts re: why Atlanta's heating is half of forced air and Pittsburgh is ~ same?
Is your baseline a VAV system with reheat? How much reheat do you have in the baseline? I'd imagine the Atlanta system would have more reheat in the summer/shoulder seasons. Also, you should compare heating between the two radiant models, not between the radiant models and their respective baselines.
Simple constant volume heating - no reheat