Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

openstudio dehumidifying with humidistat shows no effect

asked 2018-01-11 14:13:23 -0600

Prinz Qwert's avatar

Hello everyone! I am trying to make an HVAC system that keeps a relative humidity at 60%. The building is in a very humid climate therefore I need dehumidifying. I tried to proceed as described in link However when I simulate it, the humidity is still at 90-100%

I proceeded like this:

  1. I created a scedule set to a constant value 60, with 'scedule type' set to 'percent'
  2. I created a 'Setpoint Manager Single Zone Humidity Maximum' at the outlet node of the cooling coil
  3. I set the control variable in the cooling coil to 'Temperature and Humidity Ratio'

What am I doing wrong?

image description image description image description image description image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2018-01-11 14:27:36 -0600

For the humidity control to work, you need to set the actuator node name to the inlet water node to the chilled water coil.

image description

edit flag offensive delete link more

Comments

Thank you for your answer, I set the actuater node nome to the inlet node, but it still doesn't work...

Prinz Qwert's avatar Prinz Qwert  ( 2018-01-11 14:57:05 -0600 )edit
1

Maybe you need a cooling and heating setpoint schedule?

TaylorRoberts's avatar TaylorRoberts  ( 2018-01-11 15:00:06 -0600 )edit

When the zone RH> 60%, is the cooling coil water flow rate already maxed out? If so, there will be no additional dehumidification available. Are you autosizing the coil capacity? If so, the coil size is based on the zone sensible load, not the additional latent load (i.e., total load). What HVAC system type are you using? Is that model able to dehumidify?

rraustad's avatar rraustad  ( 2018-01-11 15:44:42 -0600 )edit

Doesn't the air system require a sensible load from the zone in order to operate, @rraustad? In which case cooling and heating setpoint schedules would be required, as @TaylorRoberts said.

ericringold's avatar ericringold  ( 2018-01-11 15:58:08 -0600 )edit

The water coil controller should turn the coil on if humrat > SP node humrat max. I would report the coil control node humrat and humratmax set point to see what's happening.

InitController
if ( ( Node( SensedNode ).HumRatMax > 0 ) && ( Node( SensedNode ).HumRat > Node( SensedNode ).HumRatMax ) ) {
rraustad's avatar rraustad  ( 2018-01-12 08:03:49 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2018-01-11 14:13:23 -0600

Seen: 927 times

Last updated: Jan 11 '18