Dehumidification using Hvac Template:Zone:Ideal loads airsystem
Hi! I am using HVACTEMPLATE:ZONE:IDEALLOADSAIRSYSTEM and I want to limit the temperature to 26°C and the humidity to 60%. I set the Dehumidification Control Type to constant sensible heat ratio and the Dehumidification Setpoint to 0.6. However it seems to have no effect on the humidity. Is there any way I can limit the relative humidity to a constant value ?? Thank you in advance!
HVACTemplate:Zone:IdealLoadsAirSystem,
exhibition, !- Zone Name
thermostat, !- Template Thermostat Name
Assembly HVAC on, !- System Availability Schedule Name
50, !- Maximum Heating Supply Air Temperature {C}
13, !- Minimum Cooling Supply Air Temperature {C}
0.0156, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
0.0077, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {W}
NoLimit, !- Cooling Limit
, !- Maximum Cooling Air Flow Rate {m3/s}
, !- Maximum Total Cooling Capacity {W}
, !- Heating Availability Schedule Name
, !- Cooling Availability Schedule Name
ConstantSensibleHeatRatio, !- Dehumidification Control Type
0.6, !- Cooling Sensible Heat Ratio {dimensionless}
60, !- Dehumidification Setpoint {percent}
None, !- Humidification Control Type
30, !- Humidification Setpoint {percent}
None, !- Outdoor Air Method
0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow Rate per Zone {m3/s}
, !- Design Specification Outdoor Air Object Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness {dimensionless}
0.65; !- Latent Heat Recovery Effectiveness {dimensionless}
@Prinz Qwert Are you Using OpenStudio with E+ measure?
No I just modeled it in E+