Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

How to set a node air temperature from outside as constant

asked 2018-01-01 17:32:58 -0600

Dr. Fan's avatar

updated 2018-01-02 03:04:34 -0600

I am running the energyplus example file which is named as 'DesiccantCVRh'. I draw the system diagram in the power point as shown below. In the original model, the Outside Air Inlet Node 1 is outside air node and the temperature of the inlet air is the time varying outdoor ambient temperature based on the weather file. My question is if i want to make the temperature of Outside Air Inlet Node 1 as constant like 50 degree, 70 degree....during the whole simulation, how can i do it? What objects i need to add?

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2018-01-02 02:59:03 -0600

You can input schedules to hard set the conditions of the OutdoorAir:Node, especially Drybulb Temperature Schedule Name and Wetbulb Temperature Schedule Name.

So you create two Schedule:Constant (or Schedule:Compact) and reference them in the OutdoorAir:Node.

edit flag offensive delete link more

Comments

Thank you very much for your useful advice. You are perfectly correct. When I looked at the input and output document, I missed this point. Your suggestion saves my time. Thanks again.

Dr. Fan's avatar Dr. Fan  ( 2018-01-02 06:15:47 -0600 )edit