air density value in energyplus

asked 2017-12-28 11:09:15 -0500

building_performance's avatar

What are the density value being used for supply air mass flow rate and outdoor air mass flow rate, for Controller:OutdoorAir object? Is the density standard ==1.204 kg/m3, or is a function of temperature? I output standard density volume flow rate and current density volume flow rate, and found they are different.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-12-28 13:15:02 -0500

Answered here for system node air density (here in the documentation) and here for site air density.

edit flag offensive delete link more

Comments

Thanks a lot! It solved my problem.

building_performance's avatar building_performance  ( 2017-12-28 13:22:16 -0500 )edit