The building I'm modelling in EnergyPlus is adjacent to other heated buildings. I modeled the other buildings, as adjacent thermal zones (Net part of total floor area set to No in the Zone object), conditioned by an ideal air system. When I check the results, I see the consumption of the ideal air system included in the total consumption of my building. Is there a way to exclude it from total consumption, just like I am able to exclude its area from total building area? Or, would you better recommend to model it using Other Side Coefficients as boundary conditions?

Update 01/04: I still have no solution of that problem. I need to model the adjacent zones as actual zones because I have internal windows to be taken into account. However I am still not able to exclude the energy consumption of the other zones from that of my building in the final report. Any suggestion would be highly appreciated.

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
3

answered 2018-01-04 11:42:12 -0600

I assume that you also have District Cooling and Heating in your building, otherwise it wouldn't be a problem (the Ideal Air Loads reports energy as district cooling/heating).

So I guess you need to put the ideal air loads on an Output:Meter and do the subtraction yourself in post processing.

edit flag offensive delete link more

Comments

Ok so I need to subtract it. I was just hoping to find a way to do it in the input phase, without any post-processing. I will subtract then. Thank you

jack_l's avatar jack_l  ( 2018-01-05 02:45:39 -0600 )edit
1

answered 2018-01-10 17:46:58 -0600

gmehta75's avatar

If the adjacent building is conditioned, then the shared surfaces can be treated as adiabatic. The building that you are modeling and the adjacent heated buildings - are they at different setpoints? Do yo anticipate a great amount of heat gain or loss through the internal windows?

Some good discussions here and here and here.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2017-12-11 03:55:31 -0600

Seen: 193 times

Last updated: Jan 10 '18