drop in absolute humidity when using HVAC:Template:Zone:PTAC

asked 7 years ago

hullaballoo's avatar

updated 7 years ago

Hi everyone! I am simulating an existing building with a cooling split unit, using HVAC:Template:Zone:PTAC with a SingleSpeedDX with no dehumidification unit added. However, when I look at the results, there is a huge drop in absolute humidity indoors compared to outdoors (about 10g/m3). Can anyone explain me why or how can I avoid that?

Thank you in advance!!

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 7 years ago

A DX cooling coil removes both sensible (temperature) and latent (moisture) energy from the air stream. Water cooling coils also have this same property. When using a cooling coil in your simulation roughly 25% of the energy transfer will be moisture. So the result will be that the indoors are dryer than outdoors.

Preview: (hide)
link

Comments

Thank you for your answer! Do you know if there is any way to simulate a cooling unit which removes only the sensible energy and not the latent?

hullaballoo's avatar hullaballoo  ( 7 years ago )

Well, I've never tried this but you could make the SHR = 1. You must ensure that the total capacity and air flow inputs result in a supply air condition that is on the psychrometric chart (i.e., outlet air RH < 100%).

Coil:Cooling:DX:SingleSpeed,
  1.0,                !- Gross Rated Sensible Heat Ratio
rraustad's avatar rraustad  ( 7 years ago )

Thank you now it works just fine!!