Does Ideal Air Loads affect temperature results?

asked 2017-11-09 19:45:18 -0600

Ner's avatar

In one of the models that I'm working on, I want to calculate the Zone Mean Air Temperature of a building with no HVAC, fans, or any other mechanical thermal conditioning. I'm currently running the models with Ideal Air Loads. Will the Ideal Air Loads modify in any way the Zone Mean Air Temperature, or Surface Face Temperatures?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-11-10 10:08:38 -0600

Yes, Ideal Air Loads will try to meet your thermostat setpoints. If you want to look at behavior of your building without the conditioning then you need to turn ideal air loads off.

edit flag offensive delete link more

Comments

Thank you very much for your answer, I couldn't understand what represents Ideal Air Loads in the actual building, now it's clear.

Ner's avatar Ner  ( 2017-11-16 19:29:02 -0600 )edit