Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

I have an extra setpoint manager that needs deleting? [closed]

asked 2017-11-08 20:39:47 -0500

nbjensen's avatar

updated 2017-11-09 10:34:00 -0500

I have 3 Dual Duct air loops in my model and added Multizone Heating Average setpoints on the high side the ones that I have assigned to the loops are called: SETPOINT MANAGER MULTI ZONE HEATING AVERAGE SETPOINT MANAGER MULTI ZONE HEATING AVERAGE 1 SETPOINT MANAGER MULTI ZONE HEATING AVERAGE 3

I am sure that SETPOINT MANAGER MULTI ZONE HEATING AVERAGE 2 was in one of the loops was deleted and then readded, hence the skipping of 2. When running my simulation it gives me this error:

* Severe * IP: IDF line~57069 Error detected in Object=SETPOINTMANAGER:MULTIZONE:HEATING:AVERAGE, name=SETPOINT MANAGER MULTI ZONE HEATING AVERAGE 2 * ~~~ * Field [HVAC Air Loop Name] is required but was blank

When looking at the E-Plus code itself it said that SETPOINT MANAGER MULTI ZONE HEATING AVERAGE 2 was still there, but was unassigned to a zone. Is there a way to delete this setpoint manager in OpenStudio so I no longer see this fatal error?

edit retag flag offensive reopen merge delete

Closed for the following reason the question is answered, right answer was accepted by nbjensen
close date 2017-11-16 00:46:28.028911

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-11-09 03:55:09 -0500

Avi's avatar

I think that it is known issue. Try standing on that node and see whether on the edit tab two setpoint mangers are showing up. If that is the case, and any way you could open the OSM file in text editor, search for that setpoint manager and delete it's entry.

edit flag offensive delete link more