Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

I am trying to replace an existing HVAC system (VAV with Chiller) with VRF system. Simulation runs well but gets following error "User did not pick any zone to be added to VRF". I don't know how to resolve this error. Please advice.

asked 2017-11-07 04:57:30 -0500

updated 2017-11-07 12:28:09 -0500

image description

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2017-11-07 09:52:33 -0500

Tim Johnson's avatar

Javed, this might be to obvious, but make sure you checked the box for each space type you want to be on the VRF system. It is also picky about building stories. You need to make sure that you have stories in your model and that each story includes a conditioned zone.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-11-07 04:57:30 -0500

Seen: 171 times

Last updated: Nov 07 '17