constant outdoor air change fraction in E+

asked 2017-10-25 07:41:31 -0500

khr5849's avatar

updated 2017-10-25 07:57:28 -0500

I want to let the zone take constant outdoor air fraction in E+. for example, when the zone volume is 100m3, how can i let the outdoor air 30m3 per hour constantly?

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
1

answered 2017-10-27 03:41:48 -0500

Chandan Sharma's avatar

In addition to @mdahlhausen suggestion above, take a look at ZoneVentilation:DesignFlowRate

edit flag offensive delete link more
2

answered 2017-10-25 12:23:26 -0500

I hope I'm understanding this question correctly. This is straightforward in EnergyPlus. In your SpaceType object, you can set a DesignSpecification:OutdoorAir object (documentation) and specify outdoor air flow in Air Changes per Hour (ACH) at 30/100 = 0.3 ACH. You can specify a schedule, though the default is always on, which is what you want.

edit flag offensive delete link more