solve Error relating ChillerHeater in E+

asked 2017-10-25 07:38:05 -0500

khr5849's avatar

updated 2017-10-27 03:35:15 -0500

Chandan Sharma's avatar

I made a idf file including ChillerHeater:Absoption:DirectFired. Error message said

   ** Severe  ** CalcGasAbsorberChillerModel: Condenser flow = 0, for Gas Absorber Chiller=BIG CHILLER
   **   ~~~   **  During Warmup, Environment=CHICAGO_IL_USA ANNUAL COOLING 1% DESIGN CONDITIONS DB/MCWB,

I checked condenser loop related componants, and flow rates are all 'autosized'

what is a problem? please help!!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-10-27 03:34:59 -0500

Chandan Sharma's avatar

This one probably requires opening an E+ issue. For the similar condition, though severe error is issued for chiller types EIR, reformulated EIR, central GSHP and other chillers such as electric, engine driven etc., fatal error is not issued and program runs to completion. Only ChillerHeater:Absorption:DoubleEffect and ChillerHeater:Absorption:DirectFired issue fatal error. The reason for condenser flow rate getting sized to zero could be chiller evaporator flow rate or nominal capacity or chilled water loop design volume flow rate are getting sized to zero. Unfortunately there don't seem to be a workaround except hard sizing inputs such as chiller nominal capacity and see if the file runs to completion.

edit flag offensive delete link more