Cooling energy for HVACTemplate:System:DedicatedOutdoorAir

asked 2017-10-05 04:00:16 -0500

katsuya.obara's avatar

I want to verify the result exporting air system cooling energy from the model which implement FCU and PAU(for FA supply)
However, when I export Air System Total Cooling Energy, it seems that cooling energy by PAU is not included.
Does anyone know how I can export cooling energy for PAU?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
1

answered 2017-10-05 13:52:52 -0500

Piljae Im's avatar

"Air System Total Cooling Energy" should give you "DOAS:Air System Total Cooling Energy [J]" which is a cooling energy by PAU (if this is DOAS). The cooling energy for FCU can be found by "Fan Coil Cooling Energy"

edit flag offensive delete link more

Comments

Thank you! What about the case for HVAC:System:VRF?

katsuya.obara's avatar katsuya.obara  ( 2017-10-06 02:12:41 -0500 )edit

You can use "VRF Heat Pump Total Cooling Rate"

Piljae Im's avatar Piljae Im  ( 2017-10-06 15:21:47 -0500 )edit