Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

primary-secondary heating

asked 7 years ago

gsuscalo's avatar

updated 7 years ago

I am currently using openstudio 1.14, trying to set up some HVAC details based on the documentation for my project. In my building, spaces are heated from a boiler plant in the basement, and heat is distributed through a 'primary' loop that serves the main VAV coil & zone reheat coils; while a secondary hot water loop serves a system of perimeter fin radiators & unit heaters. The secondary system pumps hot water from the primary loop. According to forum responses regarding similar attempts at primary/secondary cooling systems, this pumped-secondary-loop setup is discouraged (here).

So does the OS interface in fact not support a pump-connected secondary loop setup for hot water, and should I stick to using the HX object to 'connect' the two loops (that's what I have now)? Or is there some way that I can connect the primary/secondary loops with a pump instead of the current fluid/fluid HX?

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
2

answered 7 years ago

Chandan Sharma's avatar

EnergyPlus PlantLoop object has input field Common Pipe Simulation which specifies a primary secondary configuration. Though this field eliminates the need of specifying two different EnergyPlus loops each for Primary and Secondary half loops, it is not a recommended approach and in the future the common pipe is expected to be obsolete. A recommended approach for primary/secondary pumping arrangement is using a heat exchanger and two separate loops . Refer to Plant Application Guide Chapter 8, Example System 3: Primary/Secondary Pumping for more details. A pump is quite simply the component that drives the flow in plant and condenser loops. It doesn't connect the two loops. The thread (and E+ example file mentioned there) also have pumps in supply side inlet of both the loops.

Preview: (hide)
link

Comments

"common piping"...yes, that is the terminology I was looking for...but it sounds like it will be a pain implementing that. Thanks for clearing that up. I'll stick with the heat exchanger for now.

gsuscalo's avatar gsuscalo  ( 7 years ago )

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 7 years ago

Seen: 1,527 times

Last updated: Oct 02 '17