insert HVAV whole system measure

asked 2017-08-29 11:17:37 -0600

xzb86 gravatar image

updated 2017-08-29 16:08:19 -0600

I make a 4 room model, and willing to insert a whole system directly (VAV with DOAS). then I had 6 coils of heating and cooling. if I delete any of them and simulate, fail. anyone know where is the problem?

edit retag flag offensive close merge delete

Comments

Can you tell me which measure you used? I'm trying to add a DOAS to a VAV system but keep getting unmet load hours.

anchapin gravatar image anchapin  ( 2018-08-02 06:41:53 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
5

answered 2017-08-29 12:04:38 -0600

When you delete a coil on an air loop, the coil remains connected on the plant loop. You need to delete it there as well.

edit flag offensive delete link more

Comments

I forgot it thanks!

xzb86 gravatar image xzb86  ( 2017-08-29 21:14:09 -0600 )edit