SSR/Telecom/Server Room Equipment Power Density Assumptions

asked 2017-08-28 16:49:30 -0500

updated 2017-08-28 16:49:58 -0500

I'm looking for any assumptions on how much the equipment power density of a server/SSR/telecommunications room would use. Already looked at COMNET and didn't find anything specific to server/SSR rooms. Does anyone have any literature to point me in the right direction?

edit retag flag offensive close merge delete

Comments

2

It's always good to ask the client on the load they have for the server room as It varies WIDELY from office to office. I also don't recall any literature/standard for such loads although would love to know about it if there is.

The projects I've worked on In last couple of months, I had almost 5 kW of load for an office building with almost 625 people occupancy, and another one with 8 kW of server load with almost 1,000 people office. Both the projects are in China. A rough calculation of almost 8 Watt per person maybe for a medium/large scale office?

Harshul Singhal's avatar Harshul Singhal  ( 2017-08-28 18:53:42 -0500 )edit