How can i model hot water loop and air loop for a single zone

asked 2017-08-24 08:42:41 -0600

Hannes's avatar

updated 2017-08-25 04:43:47 -0600

I'm trying to model an existing building where each zone is heated by radiators (hot water) and a ventilation system. So each zone would need a hot water loop with coil:heating:water on the demand side and an air loop to get the heat from the water to the zone air, and in addition to that an air loop for the ventilation system. Both loops are heated by district heating and work separately from each other.

As Iread here EnergyPlus can´t handle two air loops per zone. So has anybody an idea how to model that? Can i model the coils via zone equipment?

edit retag flag offensive close merge delete

Comments

1

As an aside, note that the EnergyPlus team is working on allowing multiple air loops per zone at this very moment. So look for it in a future release!

shorowit's avatar shorowit  ( 2017-08-25 05:21:06 -0600 )edit

1 Answer

Sort by » oldest newest most voted
3

answered 2017-08-24 12:25:28 -0600

updated 2017-08-25 04:44:21 -0600

The situation in the question that you referenced does not apply to your building as you do not have two airloops feeding into your zone. The ventilation system in your case should be modeled as an air loop and the radiator should be modeled as a zone equipment.

The component Coil:Heating:Water is quite different from a radiator (as in real-life) and is not applicable to model radiators.

I suggest that you look at the example file named "VAVSingleDuctReheatBaseboard" about setting the system required to model your scenario (it is quite similar but not exactly). As you can see in the model, the component ZoneHVAC:Baseboard:Convective:Water can be used to model radiators. This in-turn is added to a plant loop (see BranchList). The Air Loop Main Branch (look under the Branch Class) in the example file would need to be adjusted based on the ventilation system of your building.

edit flag offensive delete link more

Comments

Good answer! (Please note that we have a convention on UnmetHours to not include greetings ("Hi", "thanks", etc))

Julien Marrec's avatar Julien Marrec  ( 2017-08-25 04:45:28 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-08-24 08:42:41 -0600

Seen: 233 times

Last updated: Aug 25 '17