Designbuilder/EnergyPlus Relief fan

asked 2017-08-11 07:58:01 -0500

kbk78 gravatar image

updated 2017-08-11 07:58:44 -0500

How do I setup a relief fan on the AHU in designbuilder or energyplus. The fan would need to track the outdoor air flow including increased outdoor airflow during economizer mode.

edit retag flag offensive close merge delete

2 Answers

Sort by ยป oldest newest most voted
2

answered 2018-07-16 16:53:31 -0500

Molly Curtz gravatar image

updated 2018-07-16 16:54:40 -0500

I found your question because I have the same one. In Energy Plus, I was able to add a relief fan as a component on the AirLoopHVAC:OutdoorAirSystem, just by modifying the AirloopHVAC:OutdoorAirSystem:EquipmentList and adding the Relief fan object. I started with the expanded IDF from the example file "HVACTemplate-5ZoneVAVWaterCooled.idf". I checked the hourly output variables for the fan power and the node flow exiting the fan and it seems to work. Here are the objects I modified/added:

 AirLoopHVAC:OutdoorAirSystem:EquipmentList,
   VAV Sys 1 OA System Equipment,                           !- Name
   OutdoorAir:Mixer,                                        !- Component Object Type
   VAV Sys 1 OA Mixing Box,                                 !- Component Name
   Fan:VariableVolume,                                        !- Component Object Type
   VAV Sys 1 Relief Fan;                                 !- Component Name

 Fan:VariableVolume,
   VAV Sys 1 Relief Fan,                                    !- Name
   FanAvailSched,                                           !- Availability Schedule Name
   0.7,                                                     !- Fan Efficiency
   600,                                                     !- Pressure Rise {Pa}
   autosize,                                                !- Maximum Flow Rate {m3/s}
   Fraction,                                                !- Fan Power Minimum Flow Rate Input Method
   0.25,                                                    !- Fan Power Minimum Flow Fraction
   ,                                                        !- Fan Power Minimum Air Flow Rate {m3/s}
   0.9,                                                     !- Motor Efficiency
   1,                                                       !- Motor in Airstream Fraction
   0.35071223,                                              !- Fan Power Coefficient 1
   0.30850535,                                              !- Fan Power Coefficient 2
   -0.54137364,                                             !- Fan Power Coefficient 3
   0.87198823,                                              !- Fan Power Coefficient 4
   0,                                                       !- Fan Power Coefficient 5
   VAV Sys 1 Relief Air Outlet,                           !- Air Inlet Node Name
   VAV Sys 1 Relief Fan Outlet;                             !- Air Outlet Node Name
edit flag offensive delete link more
2

answered 2017-08-16 14:15:38 -0500

Hi @kbk78

Not sure if you figured this out already. In EnergyPlus, the outdoor airflow is controlled using the object Controller:OutdoorAir . Based on how you want to model the economizer, you can look for the appropriate selection using the E+ I/O ref guide. You can then model the limits according to your system control sequence of operations.

This controller is applied to AirLoopHVAC using a AirLoopHVAC:ControllerList.

image description

Hope that answers your question!

  • Raghu
edit flag offensive delete link more

Comments

@Raghu, question is about modeling a relief fan not about modeling economizer. The return fan on the AHU moves the return air from the zone to the AHU. But the relief fan exhausts the excess air (that was brought in as outside air) from the return air to the outside to keep the airflow in balance. Though we can include a zone exhaust fan it does not pass through the AHU heat recovery coil and also the exhaust would not increase if the AHU is in economizer mode.

kbk78 gravatar imagekbk78 ( 2017-08-16 15:43:28 -0500 )edit

Could you explain the system that you are trying to model and how you intend to control it?

rsunnam gravatar imagersunnam ( 2017-08-16 15:49:46 -0500 )edit