Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

"Draft Strictness" Error when opening existing .IDF

asked 2017-08-03 10:26:07 -0600

bfrazier gravatar image

updated 2017-08-03 11:12:08 -0600

I cannot open an IDF file that was sent to me due to a "draft strictness" error. Is there a known way to remedy this?

Thank you.

edit retag flag offensive close merge delete

Comments

1

@bfrazier could you include the related lines from the error file in your post? That would help others answer your question. Are you trying to open this IDF in SketchUp or IDF Editor? Was this IDF created using an interface like OpenStudio or DesignBuilder?

Aaron Boranian gravatar imageAaron Boranian ( 2017-08-03 10:51:17 -0600 )edit

Aaron, I apologize for leaving that info out of my original post.

The error file reads as follows:

"The collection is INVALID at strictness level 'Draft', because of the errors:

Object level data error of type NoIdd. Error pertains to an object of type "Catchall", named

Additional information about the error type: Input data definition is missing or empty. Field level data error of type DataType."

The IDF was created in DesignBuilder and I am trying to import it into OpenStudio.

This is my first day looking at open studio or energy plus so i'm extremely green

Thank you for the help

bfrazier gravatar imagebfrazier ( 2017-08-03 11:31:39 -0600 )edit

1 Answer

Sort by ยป oldest newest most voted
2

answered 2017-08-08 12:57:11 -0600

One possibility for the cause of this error is that the EnergyPlus version used in your Design Builder install is a different than the EnergyPlus OpenStudio is using. EnergyPlus has different versions. You can translate an .idf to a newer version with the Transition Version option in the file menu of EP-Launch. You can check the version of an .idf file by opening the .idf in a text editor and looking at the Version identifier tag (should be the first object).

Another possibility is that you have objects in your EnergyPlus file that are not yet available in OpenStudio. If so, the error message may tell you what type of object it is having issues with.