Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

Lighting controls in Leed certification

asked 2017-08-02 04:35:02 -0500

manfred's avatar

updated 2017-08-02 05:33:59 -0500

I would need some explanations regarding the proposed building lighting control for LEED certification, particularly in Table G3.1.6.g and Table G3.2 of Standard 90.1-2007.

If I have an occupancy sensor in a surface area greater than 460 m² with a installed power of 1000 W, should I have to insert a 900W (10% less) power in my proposed building model? Is this power reduction calculated to take into account the lower energy consumption that will occur due to the occupancy sensor?

If the occupancy is greater than zero, the lighting power must be nominal or must be proportional to occupancy? Remaining in the previous example, if I have 50% occupancy, should the lighting power be 900W or 450W?

edit retag flag offensive close merge delete

Comments

(Side note: we have a convention here to not include greetings (hello, thanks, etc))

Julien Marrec's avatar Julien Marrec  ( 2017-08-02 05:33:28 -0500 )edit

1 Answer

Sort by » oldest newest most voted
5

answered 2017-08-02 05:39:06 -0500

updated 2017-08-02 05:43:35 -0500

Your proposed model has 1000 W of light power, but because you have an occupancy sensor you would install 900 W (10% less) if your area is greater than 5000 ft²/460m². You would then apply a lighting schedule, same in the proposed and baseline.


Let's say the zone is 6000 ft², an open office, and you're using the space by space area method.

  • Baseline: 6000 * 1.1 W/ft² = 6600 W
  • Proposed: 1000 W * (1-10%) = 900W
  • Both have the same schedule.
edit flag offensive delete link more

Comments

It's all clear, thank you. Just another question: is the lighting program of the on-off type or modular? For example: whether there is a single person or 400 at a given time, the lighting will always be 900W or not?

manfred's avatar manfred  ( 2017-08-02 09:45:12 -0500 )edit

The lighting will always be 900W yes. Well, 900W times whatever value is in your schedule. (Note that there is a section about changing the schedule if you can submit something valid to the rating authority...).

Julien Marrec's avatar Julien Marrec  ( 2017-08-02 10:11:44 -0500 )edit
1

Just to avoid misunderstandings, if I have 50% occupancy at a given time, the lighting at that time must be 450W [(1000W-10%) * 0,5 occupation] or 900W [(1000W-10%) * 1 occupation]? In my opinion, it should be 900 W, because even if only one person is present, lighting should not be partial.

manfred's avatar manfred  ( 2017-08-02 11:25:21 -0500 )edit

@Julien Marrec can you confirm that I'm right?

manfred's avatar manfred  ( 2017-08-03 07:36:11 -0500 )edit
1

The light schedule is left at your discretion. 90.1 User's Manual has such schedules, that you can also find in more useful format in RMI's EMIT tool, and in OpenStudio too. These schedules tend to typically somewhat follow the general pattern of occupation, but they aren't the same exactly. For eg the light schedule for a typical open office would have 5% at night (to account for 24hr lighting + maybe some lights left on by mistake) while the occupancy schedule would be zero.

Julien Marrec's avatar Julien Marrec  ( 2017-08-07 03:51:43 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-08-02 04:35:02 -0500

Seen: 160 times

Last updated: Aug 02 '17