Should infiltration air be removed?

asked 2017-07-18 12:21:13 -0500

Sllencer's avatar

updated 2017-07-18 12:45:40 -0500

Hi All,

I'm using EnergyPlus to model a zone that is being supplied with conditioned air and has infiltration (ZoneInfiltration:DesignFlowRate). I see that the flow rates for my HVAC equipment balances (e.g. HVAC air flow supply = HVAC return air flow). 1)Shouldn't the system also remove the additional air introduced via infiltration? 2) If it doesn't, does the "build of up air" skew the results (e.g. increasing the total volume of air to heat/cool in the zone)?

Thanks!

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
6

answered 2017-07-18 12:48:01 -0500

The thermal impact of infiltration is included in the zone air heat balance, but not the mass. The default zone air mass calculations do not account for infiltration, so there is no build up of air in zones as you describe. To include the mass balance, you'll need to add a ZoneAirMassFlowConservation object for your zones, or balance the flows manually. You can read more about it in the engineering reference here