Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

openstudio Cooling Thermostat assign

asked 2015-01-21 15:21:26 -0500

obuchely's avatar

updated 2015-01-22 14:06:20 -0500

Is there a faster way to assign cooling and heating thermostat schedules to a thermal zone? I am using OS thermal zone section and draging one by one from My model section. Same with zone equipment.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2015-01-21 15:51:59 -0500

It is easiest to create thermostats that have your desired heating and cooling schedules and then assign the thermostats to zones while in SketchUp: image description image description

If most all of your zones have the same thermostat you can also use the "Set Thermostat Schedules" script (best to use in OS by using the apply measure now function). This script will assign all zones to a single thermostat, and then you can go change any zones that you want a different thermostat in.

Script is located here: Set Thermostat Schedules

Also, you can edit the script to assign a thermostat to only zones of a certain space type for example.

edit flag offensive delete link more

Comments

Thanks Taylor. You save me lots of time. Is there a similar script to assign PTHP equipment to Thermal zones?

obuchely's avatar obuchely  ( 2015-01-22 13:38:24 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2015-01-21 15:21:26 -0500

Seen: 1,088 times

Last updated: Jan 21 '15