Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
3

How to add a dead-air plenum space type so that infiltration can be considered coming from it?

asked 2017-06-08 13:25:08 -0500

Julie's avatar

updated 2017-06-10 18:08:30 -0500

I have searched all over the website for a solution but I had no luck. I am currently modeling a building that has a dead-air plenum that splits the "first floor open garage" to the "second floor office area."

The plenum is a dead air service space and does not have any ventilation going in or out of it. The building is an office building with a 189.1-2009 standard.

I have modeled the plenum in sketchup already but I am trying to figure out how to make OpenStudio/EnergyPlus consider that space as an area that is affected by infiltration.

From information I found, it says that a space type would have to be given to the space. Would I give it a schedule set? Design specification outdoor air? What about Space Infiltration Design Flow Rates and/or Space Infiltration Effective Leakage Areas?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2017-06-08 14:45:44 -0500

Often if you have an unconditioned plenum space like a dropped ceiling, energy modelers just make it part of the space below, but it's fine to model the plenum as its own zone/space, and there are advantages to this approach at times.

Generally you model the plenum like other spaces but with the following exceptions

  1. Make sure to un-check "Part of Total Floor Area" for the space. This will make sure it isn't counted towards the total building area and as a result wont affect area normalized results.
  2. Make a new space type for the plenum that doesn't have any internal loads in it, except for infiltration.
  3. Create a construction set with no constructions in it and apply it to the space type. If your plenum is dropped ceiling, then add a floor construction to it that is something like acoustical ceiling tile or drywall (but not a concrete slab). Or if your plenum is more like a raised floor, then do the opposite - create a construction to use for the plenum ceiling that represents the raised floor material. OpenStudio will handle construction conflicts between the plenum and the main space so that the space has a mirrored construction to what the attic has.

Now you're all set. As usual the plenum should be part of a thermal zone. You could make it a zone by itself, or combine it with the space below, but combining it with the space below defeats the point of modeling it separately, but is nice if you want to see how much of a difference it makes to the simulation results.

The approach for an attic is very similar, but you may have ventilation in addition to infiltration, and you may have insulation on the attic floor and no insulation on the attic roof/ceiling.

One last note. If you are modeling a very complex floor plan (50 +/- or more spaces) then plenum space may end up with more than 100 surfaces which can result in a slower simulation. One solution to this is to not intersect and match the attic with the spaces below but use an adiabatic boundary condition, but with that approach there would be no heat transfer across the plenum, may make more sense to do that when it is a supply or return air plenum.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-06-08 13:25:08 -0500

Seen: 7,231 times

Last updated: Jun 08 '17