Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

why the wet bulb temperature of air is constant during the evaporative cooling?

asked 2017-06-07 08:32:36 -0500

amirrezaheydari's avatar

updated 2017-06-07 08:38:24 -0500

why the wet bulb temperature of air is constant during the evaporative cooling?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
2

answered 2017-06-07 11:36:35 -0500

The definition of the thermodynamic wetbulb is the temperature of adiabatic saturation. i.e. it is the outlet temperature of air sent through a 100% effective adiabatic cooler.

Evaporative coolers can be modeled as adiabatic coolers with a prescribed effectiveness. With minimal piping and pump heat gain, the recirculating fluid can only exchange heat with the air stream. Without a heat source/sink, the fluid will quickly come to equilibrium with the inlet air, and no net heat transfer occurs. If the inlet air is not saturated, there will be sensible and latent heat transfer, but two will always cancel each other out. By the definition of the thermodynamic wetbulb, you should expect the wetbulb to be nearly constant in any evaporative cooling model.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

1 follower

Stats

Asked: 2017-06-07 08:32:36 -0500

Seen: 1,228 times

Last updated: Jun 07 '17