Boiler nominal capacity

asked 2017-05-18 12:04:34 -0500

Nithya's avatar

Has anyone come across this issue where the total load from coil:heating:water does not add up to nominal capacity of both the Boilers? infact the load is exactly twice!
Attaching relevant images from html output! BoilerLoop coil capacity

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-05-19 01:01:28 -0500

I would bet that if you click on each of your boilers and look at the field Sizing Factor you will find a value of 1.

If you have two boilers, you should put 0.5 for each if you want both to be sized as half the plant loop load.

edit flag offensive delete link more