How to model process cooling with ASHRAE 90.1 App G Baseline system 5 or 6
I have a LEED project that I am evaluating using the Performance Rating Method in Appendix G of ASHRAE 90.1. This building meets the space, height, and primary heating criteria for the baseline model to have HVAC system 5, Packaged DX VAV w/HW reheat. As such the cooling is done via DX cooling coils and there is no CHW loop. However, there is a process cooling load for some laboratory equipment within the building design that requires CHW for cooling. How do I accomplish this with the baseline model? I see two options.
- Use HVAC system 7 instead of HVAC system 5 and follow appendix G accordingly.
- Keep using HVAC system 5 for the space conditioning and model a chw loop only for the process load using a minimally compliant water cooled chiller and pumping power according to appendix G.
I'm leaning towards option 1. If anyone has experience with this issue in their LEED submission I would be grateful to hear from you.
Edit: The proposed case hvac system uses CHW coils for space cooling and the process cooling is served by the same cooling plant consisting of air cooled chillers and dry coolers for free cooling in the colder months.