Why economizer operation does not follow Time of Day Economizer Control Schedule

asked 2017-05-08 10:17:00 -0600

katsuya.obara's avatar

Hi!
I set operation schedule specifying when air side economizer is available and set the schedule to the Field: Time of Day Economizer Control Schedule Name
However, checking at the result Air System Outdoor Air Economizer Status, air side economizer is operating even when it is specified 0(disable this feature).
I suspect that some other parameter has priority to this schedule but could not find any description in the document.
Does anyone know what is causing this situation?
Thank you.

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
4

answered 2017-05-08 12:01:06 -0600

updated 2017-10-09 08:40:44 -0600

The time of day economizer control schedule only activates economizer mode according to the schedule. It does not disable economizer operation according to other inputs.

if ( EconomizerAirFlowScheduleValue > 0.0 ) {
    EconomizerOperationFlag = true;
    OutAirSignal = 1.0;
}

So the economizer should be on anytime the schedule values are > 0. If you set other inputs to not allow economizer operation (e.g., leave other limit input fields blank, for example Economizer Maximum Limit Dry-Bulb Temperature) then the schedule should work as you expect.

edit flag offensive delete link more