Can the Duct E+ object be used to make a AirLoop demand-side bypass?
How is the E+ Duct Element typically used? I was contemplating using it as an Airloop demand bypass, similarly to a plant demand bypass with an adiabatic pipe. Tried to add it in between an exiting AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer objects, but got yelled at by E+.
AirLoopHVAC:ZoneMixer,
AHU-1 Return Air Mixer, !- Name
AHU-1 Zone Equipment Outlet Node, !- Outlet Node Name
AHU-1 Inlet Node TZ01-11, !- Inlet 1 Node Name
AHU-1 Inlet Node TZ01-12, !- Inlet 2 Node Name
AHU-1 Inlet Node TZ01-13, !- Inlet 3 Node Name
AHU-1 Inlet Node TZ01-21, !- Inlet 4 Node Name
AHU-1 Inlet Node TZ01-22, !- Inlet 5 Node Name
AHU-1 Inlet Node TZ01-23, !- Inlet 6 Node Name
AHU-1 Inlet Node TZ01-24, !- Inlet 7 Node Name
AHU-1 Inlet Node TZ01-25, !- Inlet 8 Node Name
AHU-1 Inlet Node TZ01-26, !- Inlet 9 Node Name
AHU-1 Inlet Node TZ01-31; !- Inlet 10 Node Name
AHU-1 Inlet Node Bypass; !- Inlet 11 Node Name
AirLoopHVAC:ZoneSplitter,
AHU-1 Supply Air Splitter, !- Name
AHU-1 Zone Equipment Inlet Node, !- Inlet Node Name
AHU-1 Outlet Node TZ01-11, !- Outlet 1 Node Name
AHU-1 Outlet Node TZ01-12, !- Outlet 2 Node Name
AHU-1 Outlet Node TZ01-13, !- Outlet 3 Node Name
AHU-1 Outlet Node TZ01-21, !- Outlet 4 Node Name
AHU-1 Outlet Node TZ01-22, !- Outlet 5 Node Name
AHU-1 Outlet Node TZ01-23, !- Outlet 6 Node Name
AHU-1 Outlet Node TZ01-24, !- Outlet 7 Node Name
AHU-1 Outlet Node TZ01-25, !- Outlet 8 Node Name
AHU-1 Outlet Node TZ01-26, !- Outlet 9 Node Name
AHU-1 Outlet Node TZ01-31, !- Outlet 10 Node Name
AHU-1 Outlet Node Bypass; !- Outlet 11 Node Name
Duct,
AHU Demand Bypass Duct, !- Name
AHU-1 Outlet Node Bypass, !- Inlet Node Name
AHU-1 Inlet Node Bypass; !- Outlet Node Name
************* Beginning System Sizing Calculations
** Severe ** Node AHU-1 OUTLET NODE BYPASS connects to no component
** ~~~ ** Occurs in Supply Air Path=AHU-1 SUPPLY AIR PATH
** ~~~ ** Check the connection to a ZoneHVAC:EquipmentConnections object
** ~~~ ** Check if this component is missing from the Supply Air Path
** Fatal ** Preceding errors cause termination
Thanks