Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

The cooling load of result report is 0 in openstudio

asked 2017-04-09 07:57:19 -0600

Done's avatar

updated 2017-04-13 13:48:09 -0600

I made a simple model with the ideal air load system, I only want to see the room load in the natural situation. But the cooling load from the output report is 0. Can anyone give me some tips? I have set Cooling Thermostat Schedule

edit retag flag offensive close merge delete

Comments

You need to add more detail to this question in order for people to be able to give you meaningful answers. I also don't believe people are going to contact you via that email address.

Adam Hilton's avatar Adam Hilton  ( 2017-04-10 07:46:36 -0600 )edit

1 Answer

Sort by » oldest newest most voted
4

answered 2017-04-10 16:22:57 -0600

Make sure you define BOTH a Heating Thermostat Schedule AND a Cooling Thermostat Schedule, even if you have no heating (put the heating tstat schedule to 0°C or whatever). If you don't do that, the thermostat:dualsetpoint isn't created when the model is forward translated and you end up with no cooling and no heating.

edit flag offensive delete link more

Comments

thank you! I can get the cool load while I set the Heating Thermostat Schedule.

Done's avatar Done  ( 2017-04-10 21:26:56 -0600 )edit

I'd appreciate it if you could upvote the answer if you found it helpful, and more importantly mark it as accepted since it solved your problem so that we can flag the thread as closed (please read the Help Page). Thanks.

Julien Marrec's avatar Julien Marrec  ( 2017-04-11 05:46:02 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

2 followers

Stats

Asked: 2017-04-09 07:57:19 -0600

Seen: 2,256 times

Last updated: Apr 10 '17