First time here? Check out the Help page!

Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

Load Range Based Error

asked 7 years ago

BL's avatar

I have such error message: ERROR:Invalid: Load range based components are separated by other control type components. Load Range Based should be grouped together on each flow path.

What's wrong with my model ? I think the layout is similar to the example file 5ZoneDetailedIceStorage.idf

image description

Preview: (hide)

1 Answer

Sort by » oldest newest most voted
1

answered 7 years ago

Adam Hilton's avatar

Put setpoints after each piece of equipment to get OS to create PlantEquipmentOperation:ComponentSetpoint. It's probably using PlantEquipmentOperation:CoolingLoad which isn't appropriate for this setup.

Preview: (hide)
link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 7 years ago

Seen: 211 times

Last updated: Apr 10 '17