Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
2

utility bills in the OS 1.14 GUI

asked 2017-03-30 11:44:39 -0500

mmiso's avatar

updated 2017-03-31 09:59:10 -0500

I tried to use the “Utility Bills” subtab in the “Site” main tab and defined the electricity and gas utility bills for 2016 in the OS 1.14 GUI. I expected the comparison of results (actual consumption/cost input vs. simulated (ASHRAE 90.1 templates for loads, occupancy etc.)) to show in the “Results Summary” tab under the Utility Bills/Rates part. The text at the very bottom of http://nrel.github.io/OpenStudio-user... is not very helpful. Is this expectation a mistake? Can I see the comparison elsewhere? Help/comments are much appreciated.

edit retag flag offensive close merge delete

1 Answer

Sort by » oldest newest most voted
2

answered 2017-03-30 13:01:15 -0500

In the Results Summary tab, check the drop-down box in the upper-left corner next to 'Reports:'. There should be a Calibration Report that shows the comparison of monthly energy consumption/demand against your entered utility data.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Training Workshops

Careers

Question Tools

1 follower

Stats

Asked: 2017-03-30 11:44:39 -0500

Seen: 196 times

Last updated: Mar 30 '17