Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
4

Unmet hour report error

asked 2017-03-23 22:29:54 -0500

BL's avatar

updated 2017-08-07 13:20:20 -0500

I have a zone that has 400 unmet heating hours from unoccupied period and 0 from the occupied period (2F Tolerance). However, the hourly zone mean air temperature, cooling and heating set point graph shows that the temperature never falls below the heating set point in unoccupied period. Please see attached figure. Instead, it never achieved desired occupied heating set point. Is this a reporting error from the open studio ?

Besides, any suggestions why it never achieve heating setpoint during occupied time ? (Entire system is autosized)

image description

edit retag flag offensive close merge delete

Comments

If the the 'people' in the space is always 0, then it's always counted as unoccupied. That seems to be what happening.

Adam Hilton's avatar Adam Hilton  ( 2017-03-24 08:08:00 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
3

answered 2017-03-24 08:33:33 -0500

There were several issues found with zone heating coils where the heating coil did not have sufficient capacity to meet the load, especially if ventilation is included in the input. As a workaround, I suggest manually sizing the heating coils in these zones by about 3 or 4 times what they are now.

See 6006, 6044, 6028.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

Careers

Question Tools

2 followers

Stats

Asked: 2017-03-23 22:29:54 -0500

Seen: 285 times

Last updated: Mar 24 '17