Heating Consumption is too small in ClimateZone4A

asked 8 years ago

dalin_si's avatar

updated 7 years ago

Hi, I model the baseline in OpenStudio according to ASHRAE 90.1 APP G for a apartment in NYC, the hvac system is PTAC. The heating consumption is too small to compare with cooling consumption (1:2 approx). According to the previous experience, the heating consumption is too low.

OSM file and simulation result are shown below:

model

image description

Does anyone can help me to figure out what's going on and diagnose the problem in this model?

Preview: (hide)

Comments

If your heating looks low, I would check what your outdoor air rates are. How much is being brought into each apartment zone (if any at all). Is that the amount you want? Is it being brought into the apartments 24/7?

TaylorRoberts's avatar TaylorRoberts  ( 8 years ago )

Thank you taylor

dalin_si's avatar dalin_si  ( 8 years ago )

1 Answer

Sort by » oldest newest most voted
1

answered 8 years ago

updated 8 years ago

I noticed that your PTAC system schedule in each thermal zone is set on "always on discrete". Select "Thermal Zones", pick a "Zone Equipment", go to the "edit" tab, select the gear icon to access the options. Check out "Availability Schedule Name" for each zone equipment and make sure a correct schedule is selected. I assume it will change your heating load. Let me know if it works. Otherwise, I will check it out in more details. Good luck!

image description